automation 24-09-2007, 06:22 PM ما هو الفرق بين RS 232 وال RS485 وال RS 422 ؟
وما هو الـ pt100 وال pt1000 وما الرق بينهما وكيف نستطيع ان نستخدمهم في قياس درجات الحرارة .؟
م.غزوان العوني 24-09-2007, 09:34 PM -200 to +850 °C). Standard Sensors are are available from many manufacturers with various accuracy specifications and numerous packaging options to suit most applications. Unlike thermocouples, it is not necessary to use special cables to connect to the sensor.
The principle of operation is to measure the resistance of a platinum element. The most common type (PT100) has a resistance of 100 ohms at 0 °C and 138.4 ohms at 100 °C. There are also PT1000 sensors that have a resistance of 25 ohms and 1000 ohms respectively at 0 °C.
The relationship between temperature and resistance is approximately linear over a small temperature range: for example, if you assume that it is linear over the 0 to 100 °C range, the error at 50 °C is 0.4 °C. For precision measurement, it is necessary to linearise the resistance to give an accurate temperature. The most recent definition of the relationship between resistance and temperature is International Temperature Standard 90 (ITS-90).
http://www.picotech.com/applications/graphics/pt100_sensor.jpg
This linearisation is done automatically, in software, when using Pico signal conditioners. The linearisation equation is:
Rt = R0 * (1 + A* t + B*t2 +C*(t-100)* t3)
Where:
A = 3.9083 E-3
B = -5.775 E-7
C = -4.183 E -12 (below 0 °C), or
C = 0 (above 0 °C)
For a PT100 sensor, a 1 °C temperature change will cause a 0.384 ohm change in resistance, so even a small error in measurement of the resistance (for example, the resistance of the wires leading to the sensor) can cause a large error in the measurement of the temperature. For precision work, sensors have four wires- two to carry the sense current, and two to measure the voltage across the sensor element. It is also possible to obtain three-wire sensors, although these operate on the (not necessarily valid) assumption that the resistance of each of the three wires is the same.
The current through the sensor will cause some heating: for example, a sense current of 1 mA through a 100 ohm resistor will generate 100 µW of heat. If the sensor element is unable to dissipate this heat, it will report an artificially high temperature. This effect can be reduced by either using a large sensor element, or by making sure that it is in good thermal contact with its environment.
Using a 1 mA sense current will give a signal of only 100 mV. Because the change in resistance for a degree celsius is very small, even a small error in the measurement of the voltage across the sensor will produce a large error in the temperature measurement. For example, a 100 µV voltage measurement error will give a 0.4 °C error in the temperature reading. Similarly, a 1 µA error in the sense current will give 0.4 °C temperature error.
Because of the low signal levels, it is important to keep any cables away from electric cables, motors, switchgear and other devices that may emit electrical noise. Using screened cable, with the screen grounded at one end, may help to reduce interference. When using long cables, it is necessary to check that the measuring equipment is capable of handling the resistance of the cables. Most equipment can cope with up to 100 ohms per core.
The type of probe and cable should be chosen carefully to suit the application. The main issues are the temperature range and exposure to fluids (corrosive or conductive) or metals. Clearly, normal solder junctions on cables should not be used at temperatures above about 170 C.
Sensor manufacturers offer a wide range of sensors that comply with BS1904 class B (DIN 43760): these sensors offer an accuracy of ±0.3 °C at 0 C. For increased accuracy, BS1904 class A (±0.15 °C) or tenth-DIN sensors (±0.03 °C). Companies like Isotech can provide standards with 0.001 C accuracy. Please note that these accuracy specifications relate to the SENSOR ONLY: it is necessary to add on any error in the measuring system as well.
Related standards are IEC751 and JISC1604-1989. IEC751 also defines the colour coding for PRT sensor cables: the one or two wires attached to one end of the sensor are red, and the one or two wires at the other end are white.
(http://www.picotech.com/pt100_sensors.html)
م.غزوان العوني 24-09-2007, 09:53 PM QUICK REFERENCE
FOR
RS485, RS422, RS232 AND RS423
Line drivers and receivers are commonly used to exchange data between two or more points (nodes) on a network. Reliable data communications can be difficult in the presence of induced noise, ground level differences, impedance mismatches, failure to effectively bias for idle line conditions, and other hazards associated with installation of a network.
The connection between two or more elements (drivers and receivers) should be considered a transmission line if the rise and/or fall time is less than half the time for the signal to travel from the transmitter to the receiver.
Standards have been developed to insure compatibility between units provided by different manufacturers, and to allow for reasonable success in transferring data over specified distances and/or data rates. The Electronics Industry Association (EIA) has produced standards for RS485, RS422, RS232, and RS423 that deal with data communications. Suggestions are often made to deal with practical problems that might be encountered in a typical network. EIA standards where previously marked with the prefix "RS" to indicate recommended standard; however, the standards are now generally indicated as "EIA" standards to identify the standards organization. While the standards bring uniformity to data communications, many areas are not specifically covered and remain as "gray areas" for the user to discover (usually during installation) on his own.
SINGLE-ENDED DATA TRANSMISSION
Electronic data communications between elements will generally fall into two broad categories: single-ended and differential. RS232 (single-ended) was introduced in 1962, and despite rumors for its early demise, has remained widely used through the industry. The specification allows for data transmission from one transmitter to one receiver at relatively slow data rates (up to 20K bits/second) and short distances (up to 50Ft. @ the maximum data rate).
Independent channels are established for two-way (full-duplex) communications. The RS232 signals are represented by voltage levels with respect to a system common (power / logic ground). The "idle" state (MARK) has the signal level negative with respect to common, and the "active" state (SPACE) has the signal level positive with respect to common. RS232 has numerous handshaking lines (primarily used with modems), and also specifies a communications protocol. In general if you are not connected to a modem the handshaking lines can present a lot of problems if not disabled in software or accounted for in the hardware (loop-back or pulled-up). RTS (Request to send) does have some utility in certain applications. RS423 is another single ended specification with enhanced operation over RS232; however, it has not been widely used in the industry.
DIFFERENTIAL DATA TRANSMISSION
When communicating at high data rates, or over long distances in real world environments, single-ended methods are often inadequate. Differential data transmission (balanced differential signal) offers superior performance in most applications. Differential signals can help nullify the effects of ground shifts and induced noise signals that can appear as common mode voltages on a network.
RS422 (differential) was designed for greater distances and higher Baud rates than RS232. In its simplest form, a pair of converters from RS232 to RS422 (and back again) can be used to form an "RS232 extension cord." Data rates of up to 100K bits / second and distances up to 4000 Ft. can be accommodated with RS422. RS422 is also specified for multi-drop (party-line) applications where only one driver is connected to, and transmits on, a "bus" of up to 10 receivers.
While a multi-drop "type" application has many desirable advantages, RS422 devices cannot be used to construct a truly multi-point network. A true multi-point network consists of multiple drivers and receivers connected on a single bus, where any node can transmit or receive data.
"Quasi" multi-drop networks (4-wire) are often constructed using RS422 devices. These networks are often used in a half-duplex mode, where a single master in a system sends a command to one of several "slave" devices on a network. Typically one device (node) is addressed by the host computer and a response is received from that device. Systems of this type (4-wire, half-duplex) are often constructed to avoid "data collision" (bus contention) problems on a multi-drop network (more about solving this problem on a two-wire network in a moment).
RS485 meets the requirements for a truly multi-point communications network, and the standard specifies up to 32 drivers and 32 receivers on a single (2-wire) bus. With the introduction of "automatic" repeaters and high-impedance drivers / receivers this "limitation" can be extended to hundreds (or even thousands) of nodes on a network. RS485 extends the common mode range for both drivers and receivers in the "tri-state" mode and with power off. Also, RS485 drivers are able to withstand "data collisions" (bus contention) problems and bus fault conditions.
To solve the "data collision" problem often present in multi-drop networks hardware units (converters, repeaters, micro-processor controls) can be constructed to remain in a receive mode until they are ready to transmit data. Single master systems (many other communications schemes are available) offer a straight forward and simple means of avoiding "data collisions" in a typical 2-wire, half-duplex, multi-drop system. The master initiates a communications request to a "slave node" by addressing that unit. The hardware detects the start-bit of the transmission and automatically enables (on the fly) the RS485 transmitter. Once a character is sent the hardware reverts back into a receive mode in about 1-2 microseconds (at least with R.E. Smith converters, repeaters, and remote I/O boards).
Any number of characters can be sent, and the transmitter will automatically re-trigger with each new character (or in many cases a "bit-oriented" timing scheme is used in conjunction with network biasing for fully automatic operation, including any Baud rate and/or any communications specification, eg. 9600,N,8,1). Once a "slave" unit is addressed it is able to respond immediately because of the fast transmitter turn-off time of the automatic device. It is NOT necessary to introduce long delays in a network to avoid "data collisions." Because delays are NOT required, networks can be constructed, that will utilize the data communications bandwidth with up to 100% through put.